Inner float, the deviation is too large. The tank is at 25% full
Reply #22016-11-09
The standard method is disassembly and calibration by hanging weights. If you find it too troublesome, you can use the process requirements to take the time to zero the underground tank and fill it to calibrate its range; however, process engineers usually ignore such a method of calibration, so you have to find another way to disassemble it yourself.
Reply #32016-11-09
Recalibrate it according to the instructions.
Reply #42016-11-10
If you’re not afraid of the hassle, it should be removed to create a fake cylinder, which can then be used to make adjustments with water.
Reply #52016-11-18
There are generally two methods for testing floats: the dry testing method, which involves using weights, and the water testing method. If you want to be prepared, the dry testing method is recommended

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.