Regarding instrument enclosures

2017-03-17View Original

Thread Content

When using instrument junction boxes, I encounter some grounding issues; I’m seeking solutions, thank you: 1. Is a grounding jumper wire necessary? Is there a source for the standard? 2. Is it necessary to use a piece of yellow-green wire to create a connection between every two trough boxes, or does it refer to connecting the trough boxes to the support brackets (such as angle steel)? 3. How far apart should the wires that connect the trough boxes and brackets be installed? Is there a source for the standard?
Reply #22017-03-17
Refer to the Code for Construction and Quality Acceptance of Automated Instrumentation Projects GB 50093-2013
Reply #32017-03-17
GB 50575-2010 Code for Construction and Acceptance of 1 kV and Below Distribution Engineering also specifies this in detail in 4.5
Reply #42017-03-18
The tray sections are bridged together with yellow-green wires. The entire cable tray, if it is 30 meters or less in length, needs to be grounded.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.