2018-10-28View Original

Thread Content

This post was last edited by zhengmessage on 2018-10-28 at 17:56. A 644 temperature sensor was replaced on-site, and after the replacement it always displayed 110°C (with a range of 0–100°C). After entering 475, checking the overview shows that the temperature is 27°C, which is normal, but the current output value is 21mA. Upon testing, it was found that the thermometer was functioning properly and the DCS channels were also normal; however, the output corresponding to temperature changes did not change, showing a false value of 21mA continuously. (The temperature change means that even when the temperature is not connected, it still shows 21mA.) Does anyone know what’s causing this? I see someone posted a question before, but there was no answer; others said that another sensor channel needs to be blocked? Does it work? I see that there is indeed a message on the 475 indicating something like a sensor 2 alarm. How to operate the shield channel on 475 HART? Which menu? Thank you!
Reply #22018-10-28
The 644 model you chose supports two sensors, right? If you specify sensor 2, that’s usually the case. Can’t you simply disable sensor 2 in the configuration menu?
Reply #32018-10-28
This is the type being used – a temperature-sensitive module. How do I operate it in shielded mode? It’s not available in 475
Reply #42018-10-28
Is it still showing 475 right now? Take a screenshot of the configuration interface to take a look
Reply #52018-10-28
The temperature control unit has been taken back inside the house for testing, but since it’s now time to leave work, I can only wait until tomorrow\ud83d\ude05
Reply #62018-10-28
The one you ordered is designed to hold two units, but is it actually being used with just one unit, or is the other one broken?
Reply #72018-10-28
In practice, only one is used (on one side, for wiring)
Reply #82018-10-28
Is there an error in the sensor type configuration? With thermal resistors, the issue lies in the wiring; with thermocouples, it’s the model that matters. The second sensor is a temperature sensor built into the temperature-sensitive element; it is used for cold-junction compensation when thermocouples are employed, while it is not necessary when thermal resistors are used.
Reply #92018-10-28
I’m also suspecting a configuration issue now, but I’ll just set the wiring type and range and change the tag number; I’m not too familiar with the rest.
Reply #102018-10-28
Just set it to not use in configuration>manual setup>sensor2

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.