What signals does the GDS need to transmit to the fire alarm system?

2022-08-15View Original

Thread Content

As the title suggests, there’s another question: isn’t the gas detection and alarm controller something different from a GDS?
Reply #22022-08-15
GB-50493 requires a secondary alarm signal for combustible gases and a fault signal for the GDS alarm control unit
Reply #32022-08-15
Is the secondary alarm signal generally sent to the fire alarm system? Is the fault signal hard-wired?
Reply #42022-08-15
Are they all hardwired? If there are many sensors at the site, won’t that require many wires for the secondary alarm signals?
Reply #52022-08-15
To connect a hard wire from the GDS to the fire alarm system, just one set of wires is sufficient. As long as there is a gauge in the GDS for combustible gases that has a secondary alarm function, the signal from that gauge will trigger an alarm; not every gauge’s secondary alarm signal is sent to the fire alarm system.
Reply #62022-08-15
5.1.2  The second-level alarm signals for combustible gases and the fault signals from the alarm control unit shall be sent to the fire control room for graphical display and alarm. Combustible gas detectors cannot be connected directly to the input circuit of a fire alarm controller.
Reply #72022-08-15
Is it to create an interlock logic in the GDS and then output a digital signal to the fire alarm?
Reply #82022-08-15
It may vary from one GDS manufacturer to another, but in the end it is the GDS that outputs a digital signal to the fire alarm

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.