HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Siemens integral-proportional control valve

2016-10-18View Original

Thread Content

The actuator is SAX61.03; the handwheel used for manual adjustment allows the valve to be opened and closed properly. Using PLC to control the given valve-shutting command fails to fully close the valve; the actuator stops before completing its travel, and the valve position feedback of 2.2 indicates steam leakage, rendering it unusable. I just bought it. Has anyone used this type of valve before? How do I adjust the zero point?
Reply #22016-10-18
What brand is the valve positioner?
Reply #32016-10-18
The electric actuator from German Siemens, model SAX61.03, is simply referred to as sax61.03
Reply #42016-10-18
Check to see if the actuator has reached its limit; also, use a multimeter to measure the input current....
Reply #52016-10-18
The actuator uses DC0-10V for its input and output signals; a signal generator was used to test the input voltage, but the feedback voltage corresponding to the valve position could not reach 10V – the maximum value measured with a multimeter was only 9.7V. It was observed that the actuator required a movement of 2 mm in order to close. The technician from the distributor left, and thus no solution could be found
Reply #62016-10-18
It was observed that the gear below the handwheel disengaged before reaching the predetermined (specified signal) position; the actuator only disengages when it reaches its limit value during the power-on self-check
Reply #72016-10-19
It is recommended to check the PLC’s output to see if there is any voltage drop in the wiring
Reply #82016-10-19
I tried it with a signal generator; the actuator receives a voltage signal and there is no voltage drift, and the supplier doesn’t understand this either
Reply #92017-08-30
(1) Slow valve operation. The most likely reasons for this are air leakage in the valve’s air chamber, or the presence of impurities such as mud inside the valve body, which can cause blockages. It may also be necessary to check whether the valve’s packing is too tight. (2) Leaks at the valve connections and packing areas. What needs to be checked here is whether the valve packing has aged or deteriorated; it’s also necessary to examine whether the valve stem is damaged, if there are any issues with the sealing gaskets, whether the valve packing cover is properly tightened, and whether the screws at the connections are loose. (3) Unstable operation of the control valve: Instability in the valve’s performance during operation is often caused by factors such as the pressure of the air supply; it may also be due to unstable output from the positioning device, or it could be caused by other issues. We need to check for leaks in the valve’s pressure reducer and in the pipelines, as well as whether the spring stiffness of the actuator’s execution mechanism is appropriate. The friction force on the valve stem must be high enough. (4) The diaphragm head of the valve sends a signal but the valve does not operate. This issue does not occur by chance; when it happens, we need to check whether there is any sticking in the valve’s spool and bushing, or in the valve seat. Sticking can also occur in the upper and lower guides of the valve, so thorough inspection is necessary. Additionally, any impurities or debris present in the pipelines and valves must be removed promptly. Rust on the gland surrounding the packing can also cause sticking. (5) Oscillation of the valve is accompanied by a buzzing sound. When abnormal noise occurs during operation, it is likely necessary to check whether there are any vibration sources in the vicinity and whether the valve is properly supported. Regarding the medium, it is important to ensure that its flow direction is the same as the direction in which the valve closes. It is also necessary to verify whether the CV value selected for the valve is too high; the pressure difference across the valve should not be excessive. (6) Inadequate sealing after the valve is closed. Problems of this kind usually occur because the output of the valve’s actuator does not reach its maximum value, or because the preload of the zero-point spring is too high or the valve stem is too short. In such cases, it is also necessary to check for any leaks in the bypass system, as well as to determine whether the valve seat has suffered wear or corrosion. Regarding issues related to pressure differences across the valve, it is important to ensure that the output force of the actuator is sufficient. Additionally, it is necessary to check the diaphragm for air leaks; if any leaks are detected, maintenance should be carried out promptly.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.